Anyone experience with using a temperature sensor in the floor the monitor the heating/cooling and prevent condensation ?
The sensor connected to the VMB7IN would monitor the floor temperature and adjust the target temperature of the room to the floor temperature.
The floor temperature should never be 5 DegC lower than the room temperature.
I don’t know if this helps you, but I’ve got a site meeting tomorrow to discuss something similar.
The underfloor heating installer will only allow me to use Velbus to control the whole heating system if I can monitor the floor slab temperature.
They insist that the heating (zone) must switch off if the floor temperature rises above 27°.
I’ve proposed to convert the resistsnce of an in-floor temperature sensor and convert it to pulses.
Then set an alarm threshold on a pulse reading input of a VMB7IN to temporarily lock out the relay for the zone.
The prototype circuit seems to work, I just need to calibrate it a bit more to get the resolution / accuracy they are demanding.
I’ve used a 35° thermo switch to monitor a water pipe, but it has +/- 5° accuracy and a reset temperature -10° below its trigger temperature.
How quickly do you need a solution?
As I believe there is a new module in development that would solve both of these issues and many more.
If you need more logic, then an OpenRemote rule should do the trick.