Velbus termination points

Hello,

I think i will install the Velbus with different loops for each surface of the house (two loops on ground floor, one loop on firts floor and one loop on second floor). I will do this to avoid a lot of searching in case there is something wrong on the bus (bad VMB8, …etc). My question now is : do i have to put a termination on each loop or do i simply put one termination on the longest loop (second floor) and one termination in the main board ?

Make sure that all loops have a common ground.
We’d recommend a max. of 3 terminators, starting with the most remote location.