Everything works as expected on our test setup, there must be an element that is different in your case. What build of VMBGPO do you have? Could we have your project file or part of your project file?
Can you describe your scenario in more detail? Be sure to include saving, loading, connecting, disconnecting, reading, writing, opening/closing of your project.
the configuration is fine now,
but i never see a temperature transmitted …
any update on this?
can you guys reproduce this?
anything from velleman?
setting and reading of the configuration works now, but the transmit of the temperature is not working if i set it to every time it changes …
I have your module here and it behaves as expected. Whenever the temperature changes, the temperature keeps being sent over the bus, as it should.
Any particular tests we can do as we can not reproduce the problem as you described…
well i’m not doing anything special …
you received the module i sent you, and you did not change a thing in the configuration and it worked?
I configured it for send on change and send in 10s intervals, both worked as expected. I will perform some more tests tomorrow.
i tested it again on my vmbgpo i have at home,
if i set it to run every 10 seconds => it works
if i set it to run on change => nothing happens
i placed a vmb1ts next to the vmbgpo and set that to sent on every change, the messages from the vmb1ts are seen, but i never see messages from the vmbgpo (ran it for 6 hours)
Still working today…
ok,
anything i can do to check what exactly happens here at home?
Is there any way you can record your actions or your screen?
Not sure how to create a video …
and what i see is that if i start with a new empty project the ‘Every time it changes’ radio field is not set. None of these radios are set when i read out the module in an empty project. It probably has something todo with that.
velbuslink: 8.35.0.2770
i’m unable to create a decent movie, but here is some screenshots that explain perfectly what happens …
the start, temperature is 18 degrees:
http://cereal.sinners.be/public/VelbusLink%208.35.0-1png.png
The module is set to transmit every time:
http://cereal.sinners.be/public/module.png
after some time we have this:
http://cereal.sinners.be/public/VelbusLink%208.35.0-2.png
and the velbus log:
cereal.sinners.be/public/velbuslink_10-01-2014.log
so no temp received, now if i look at the glass panel, it says 18,5 degrees, if i refresh in velbuslink (collapse and expand the module) i get this:
http://cereal.sinners.be/public/VelbusLink%208.35.0-3.png
now velbuslink is displaying the temp correctly.
i hope this will be enough to find the problem.
here is the memory dump in the vlp file:
<Module build="1325" address="65,66,67,68,69" type="VMBGPO" serial="5446" locked="0" layer="0"> <Caption>VMBGPO</Caption> <Remark></Remark> <Memory>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</Memory> <Snapshot>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</Snapshot> </Module>
Any info about this?
A difference of .5 degrees is not very spectacular… try influencing the temperature a bit more for a proper test. Also, perform a full write (not write changes) on the VMBGPO module.
i did this test during a temp increase from 14 to 20 degrees, so i had 6 degrees as a difference.
Every time i witie the module i do a full write and i cut the power to the bus for about 20 seconds before i start the test
If you cut the power after the write, the module may not have stored the setting permanently yet. Please test without cutting the power, since this is useless anyway.
ok,
did a test without cutting the power, same result
i wanted to do another test,
and i noticed that the sometimes the radio button saying that the temperature has to be sent every time it changes is not always checked when i open the configure module dialog.
None of the radios are checked at that time.
i suspect that something is wrong with this (velbuslink) and not with the module itself.
is there another way of making sure that the correct settings are sent to the module?
This could happen for instance if you first scan the module without reading memory. When configuring your own module, I have never had it not work, that is why I don’t understand the problem. Perhaps it would be best to invite a Velbus installer to take a look and diagnose your installation.